euphoria_82
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

Quote:
Originally Posted by JohnS
Lets avoid issues of the "power factor" of the load, and assume power factor is 1, so 180 KVA = 180 kW.

213 g/kWh x 180 kW = 38340 g/h or 38.340 kg/h
A liter of diesel fuel is about 0.85 kg, so 45.1 L/h or 11.9 US gallons per hour at full load. If generator is not putting out full load, consumption will be less, but not linearly with load (it still consumes fuel just to spin, even if no load is connected.)
Thanks a lot John..You made it really simple.

I applied the same logic to calculate the consumption for a Air Conditioning Unit (115 Tons) that had "Specific fuel consumption at maximum torque : 200 g/KWh.". Here the output of the engine was expressed in BHP. I simply converted BHP to KW (Mulitplied BHP by 0.7457 to get KW) and then got the calculation done as you mentioned

Thanks all the way from India
Reply With Quote
  #12  
Old 03-24-2010, 11:00 AM
Unregistered
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

Dear A+,

I had to do the conversion this moring for myself. Back to basics.
I used info available at various conversion sites and please feel free to check my figures.

1 gram = .0001 Kg
1 Kg = 2.2046 lbs
7.2 lbs = 1 gallon of diesel

1 gram or .001 Kg x 2.2046 lbs/Kg = .0022046 lbs.
.0022046 lbs x 1 gal /7.2 lbs = .000306 gallon

So 1 gram = .000306 gallon

Your consumption is given in g/kWh and you want gal/kWh so the only thing that changes is from

So let's take a consumption of 211 g/kWh x .000306 gallon = .064566 gallon and your genset is rated at 180 kW = 11.62 gallons per hour


Hopes this helps


Quote:
Originally Posted by A+ Ano View Post
I am trying to compare fuel consumption ratings on Diesel electric generators
The american ones show gals per hour of consumption at 50% load 75% load & 100% load which is what I am familiar with.
All the other generator sets are rated by g/kwh which I think is grams per Kilowatt hour?
What I'm having trouble with is a gram is a weight not a volume? Do I multiply the total kilowatt hours which in this case is 60kw x the grams per hour(in this case 230) 60x230=13,800 grams
Do I have to figure out what a gal of diesel fuel wieghs? and the convert the grams to weight?

Any help would be great.
Thanks A+
Reply With Quote
  #13  
Old 08-05-2010, 03:45 AM
Unregistered
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

Rated Power kva 20
Max power kva 22.5
PHASE three
Frequency (HZ) 50HZ
Rated voltage (V) 220~240/110~120;400/230V
Rated Current (A) 34.7A
Bore*Stroke 100x115
Displacement(L) 3.61
12h Power kw(ps) 26.5
Fuel Consumpion g/kw* h 258.4
LUBE CONSUMPTION g/kw h 2.04
Compression ratio 18.0:1

Hi, please help me I need to know what is the fuel consumption in litres for the above specs
Reply With Quote
  #14  
Old 08-05-2010, 09:09 AM
JohnS JohnS is offline
Double Ultimate Supreme Member
Long Time Member The Golden Calculator Award Over 5000 Posts
 
Join Date: Dec 2007
Location: SE Michigan, USA
Posts: 8,711
Rep Power: 17
JohnS will become famous soon enough
Default Re: g/kwh to gal/h

Quote:
Originally Posted by Unregistered View Post
Rated Power kva 20
Max power kva 22.5
PHASE three
Frequency (HZ) 50HZ
Rated voltage (V) 220~240/110~120;400/230V
Rated Current (A) 34.7A
Bore*Stroke 100x115
Displacement(L) 3.61
12h Power kw(ps) 26.5
Fuel Consumpion g/kw* h 258.4
LUBE CONSUMPTION g/kw h 2.04
Compression ratio 18.0:1

Hi, please help me I need to know what is the fuel consumption in litres for the above specs
Lets assume power factor = 1, so rated power is 20 kW. At 20 kW, fuel consumptuion is
20 kW x 258.4 g/kWh = 5168 g/h or 5.168 kg/h
Diesel varies, but 0.84 kg/l is a good typical figure for #2 diesel, so
5.168 kg/h x 1 L/0.84 kg = 6.15 L/h
Reply With Quote
  #15  
Old 02-21-2011, 05:54 AM
Unregistered
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

I need to conver 320g/kW.h into L/hr for a diesel generator 13kVa , at 50Hz with an output voltage of 230V.
Reply With Quote
  #16  
Old 02-21-2011, 07:05 AM
JohnS JohnS is offline
Double Ultimate Supreme Member
Long Time Member The Golden Calculator Award Over 5000 Posts
 
Join Date: Dec 2007
Location: SE Michigan, USA
Posts: 8,711
Rep Power: 17
JohnS will become famous soon enough
Default Re: g/kwh to gal/h

Quote:
Originally Posted by Unregistered View Post
I need to conver 320g/kW.h into L/hr for a diesel generator 13kVa , at 50Hz with an output voltage of 230V.
If we assume output is actually 13 kVA and power factor is 1 (worst case), it is 13 kW x 320 g/kW·h = 4.16 kg/h As density of diesel fuel is around 0.85 kg/L, that is 4.9 L/h at max power. If at less than max output power, consumption will be somewhat less.
Reply With Quote
  #17  
Old 03-29-2011, 06:06 PM
Unregistered
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

JohnS, in your last post you divided 4.16 by 0.85 to get 4.9. Shouldn't you have multiplied 4.16 by 0.85 to get 3.54............or am I mixed up?
Reply With Quote
  #18  
Old 03-30-2011, 03:08 AM
JohnS JohnS is offline
Double Ultimate Supreme Member
Long Time Member The Golden Calculator Award Over 5000 Posts
 
Join Date: Dec 2007
Location: SE Michigan, USA
Posts: 8,711
Rep Power: 17
JohnS will become famous soon enough
Default Re: g/kwh to gal/h

Quote:
Originally Posted by Unregistered View Post
JohnS, in your last post you divided 4.16 by 0.85 to get 4.9. Shouldn't you have multiplied 4.16 by 0.85 to get 3.54............or am I mixed up?
4.16 kg/h x 1 L/0.85 kg = 4.9 L/h

I recommend always leaving the units attached to the numbers and working the units cancellation; it is always clear whether to multiply or divide. You can still make errors by using wrong conversion factors, but it is much easier to check all the inputs to the calculation.
Reply With Quote
  #19  
Old 03-30-2011, 11:59 AM
Unregistered
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

Right you are. Thanks for the clarification.
Reply With Quote
  #20  
Old 03-02-2012, 04:56 AM
Unregistered
Guest
 
Posts: n/a
Default Re: g/kwh to gal/h

If a 500 kW diesel generator has a fuel consumption of 208 g/kWh at full load. How much it will be at 50% and 25% load? Thanks
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -8. The time now is 11:00 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2013, Jelsoft Enterprises Ltd.
Copyright ©1997-2005, 2007, OnlineConversion.com